gfci 15 amp outlet 20 amp passthrough

Joined
Nov 28, 2020
Messages
424
Reaction score
52
Country
United Kingdom
While we wait for a US electrical guy to turn up, I'll guess that it means it's rated to supply 15A but is OK connected to a cable with 20A flowing in it (i.e. supplying other outlets). That's the principle of the mustn't-overheat-tests that UK sockets have to pass to comply with the required standard.

It will be absolutely fine on a 15A breaker.
 
Joined
Nov 27, 2017
Messages
12
Reaction score
0
Thanks for your reply.. I put it in. Fels good to have expert advice!
 
Joined
May 15, 2021
Messages
397
Reaction score
47
Country
Canada
If you presently have it on a 15-breaker, leave it as is. The 20-amp is only for people whom have additional "downstream" loaded connected to the "LOAD" terminals on the back of the GFCI.

In other words, if weren't tripping the circuit breaker (or the GFCI button) before the removal of the stained devices, your present is fine.
 