1
Reaction score
0
Our Valiant boiler water pressure is low (way low - down to 0). We've topped it up before - know where the tap is etc, but it's so long ago that I can't remember:
Do we have to turn the boiler off first or let it cool down etc.?
 
Joined
Feb 4, 2011
Messages
99
Reaction score
0
If you fill the system up whilst it is hot you never know what pressure it wall fall back to when it has cooled down. So ideally fill to approx 1 bar when cold.

If filling loop is remote it could be anywhere but usually by the boiler look for a silver coloured flex with valves on each end.
If it is built in then look under the boiler where all the pipes go in and you should see a thin flexi pipe there or even a very thin copper pipe.
 