Will one RCD socket protect others??
Mark
Some time ago I fitted a new socket outlet in my son's bedroom. I had
no desire to go into the wall and hook into the existing ring main so
I decided to tap in somewhere else. Basically I tapped into the
immersion heater supply in the airing cupboard, (fused 30amp at the
consumer unit). Then I went through a 13amp fused spur, then up into
the attic, and then down into the bedroom using mini trunking, and
finally connected an RCD protected double socket. Everything fine.
Now I need to do the same in my daughter's room. My question is, if I
wire in parallel from the feed to the socket in my son's room do I
need to use another RCD protected socket? Or will the RCD in my son's
room provide protection for a regular parallel socket.
Safety is paramount of course but I don't want to spend 20 odd quid on
another RCD socket if I don't need to.
Incidentally the sockets are only for hi-fi/TV so I doubt the combined
load will ever exceed 5 amps.
ARWadsworth
Years ago (and I am not grey haired yet) when I was a child my Dad put
another socket in my bedroom for the TV I got as an Xmas present. It was one
of the things I failed his PIR this week as this socket ran from the
immersion. He wants to sell his house and I will have to work like hell over
Xmas to put the electrics right due to these type of bodges.
Do the job properly or not at all. Break into the ring main.
Adam
Sparks
consumer unit).
What size cable is this circuit using - 4mm or more I hope, if it is 2.5mm
you need to replace the 30A MCB with a 20A one, unless the immersion is on
it's own 2.5mm ring.
If you have an immersion, I hope this is connected with an FCU, fused at 13A
(Unless you have the unlikely scenario of an immersion heater greater than
3KW)
Possibly fine, if the immersion heater cable is 4mm (or more) or on a 2.5mm
ring.
Unless the socket in your son's room has a dedicated RCD protected output,
and you use this, you need another RCD socket, or just replace the fused
spur with one of these.
http://www.tlc-direct.co.uk/Products/CM4904.html (Then any further additions
will be protected)
If you just connect a normal socket to the same terminals the existing
socket is being supplied with, it will not be protected.
This is irrelevant, you are providing a 13A socket, it needs to be able to
support this load - someone may plug in a heater at some point.
Sparks...
(Not an electrician)
Mark
Sorry my mistake, the immersion heater is on a 16 amp mcb, it's the
electric oven that's on a 30 amp mcb.
We haven't used the immersion heater in 8 years and have no intention
of doing so, so as far as I'm concerned it's a spare supply. In the
event we have to use it in an emergency then the spur I've taken of it
will be switched off.
Mark
Thanks for your reply.
My mistake, the immersion is on a 16A mcb, it's the electric cooker
supply that's on a 30amp mcb.
3KW)
Yes the immersion has its own FCU in the airing cupboard with a 13amp
fuse
ring.
will be protected)
Thanks for the recommendation
Why not? Isn't the RCD measuring earth leakage irrespective as to
whether something is plugged in 'in front of it' or 'behind it'?
Yes, and if the load is over 13amps the fuse in the spur blows, I
don't see a problem here as long as the cable itself is correctly
rated?
Mark
Adam
Sorry, did you intend to answer my question or just lecture me on what
you consider to be the correct way to do the job?
Shouldn't you be in the airing cupboard fixing the "bodge"?
Sparks
fuse
No,
If that were the case, your whole house and all the people on the same phase
as you would be protected by your RCD socket.
The socket is measuring the differance in current at it's output, it can't
control what goes into it. - are you sure you should be messing with this,
no offence, but you don't sound like you should be.
rated?
There may be some regulations about not being able to apply diversity to
circuits with fixed loads on (The heater in this case) but I don't know, I
wouldn't do it this way myself, unless the heater was decommisioned.
With your immersian heater on, assuming it is 3KW, you only have 3A (700w)
of spare capacity before the MCB is at it's marked limit - You can probably
uprate this MCB to a 20A, but this still only allows 7A with all at full
chat.
....and it doesn't sound like you should be poking about in the consumer unit
anyway!
The ideal way to do it is to either tap into an existing ring (Only one
double socet per tapping, unless you fit a spur in-between, then you can fit
as manu as you like downstream) or run a new circuit from the consumer unit.
Part P will apply.
Sparks...
Sparks
If "ARWadsworth" is doing a PIR, then he is probably a qualified
electrician, so his "lecture" as you put it, is not necessarily the way he
"consider to be the correct way to do the job" but may well be the legal
way to do so.
By your comments earlier, it does sound like you should either leave it
alone and get a qualified electrician to do it, or just ask questions BEFORE
you start, and only tackle the job once you are confident you have learned
all you need to know to complete the job safely.
Throwing a strop when someone suggests what you have posted is wrong, is not
going the right way towards getting help.
Sparks...
Mark
OK, additional RCD socket it is then.
Thanks for your input.
PS, should have mentioned, immersion heater is never used, never has
been, never will be.
Sparks
Good
Disconnect it then, then everyone will be happy and you will (probably) be
compliant.
(Assuming you have sleeved the earth wires with green/yellow, stuck one of
these on your consumer unit if you are using new colours
http://www.tlc-direct.co.uk/Products/TLLAB50.html, and used 2.5mm cable
without any inaccessible screw joints. (Maybe some other factors too)
Sparks...
Sparks
Sparks said:
Good
compliant.
Sparks...
....and I would suggest you replace the spur with an RCD one rather than
getting a second RCD socket, then if you add another socket to this circuit
at a later date, you won't need to buy a third RCD socket.
As the new sockets are protected with a fused spur, you can add as many
sockets as you like, where you like, so you can just add a second double
socket to each room, off of the current socket, to save having to use
trailing extension leads, if you leave the FCU as it is, any additional
sockets would need to be the expensive RCD ones (If you want to RCD protect
them, as it is not actually needed, assuming you are upstairs)
Or, if you change the power source at a later date to come from the ring
(like it really should) then you won't have to remove the RCD sockets
(assuming your ring is currently RCD protected)
If you do change the FCU to an RCD FCU, you should replace the current RCD
socket with a normal one, as you shouldn't cascade RCD's)
Sparks...
John Rumm
john said:
Single 2.5mm cable is only rated at 23 amps.
27A if surface wired. However in the case overload protection would be
provided by the 13A fused spur. In spite of the high sounding rating,
fault protection for the 2.5mm T&E would probably be provided by the 30A
fuse at the CU (although one ought to do the calculations to prove it)
The immersion circuit should be on a 16 amp mcb.
That would depend on the size of the immersion heater(s).
with no other supply taken
from it !
Ideally, but suitably labled at the CU this would not be a big problem
ARWadsworth
That was not a lecture as I am not a professor but you are a twat and a
bodging twat at that
I will be there over Xmas.
I hope your house burns down due to shit electrical work and your daughter
is killed by the Ipswich serial killer
Merry Xmas
Adam
John Rumm
What exactly are you trying to achieve here? Is it a case you have young
children and you are worried they might go sticking conductive things in
sockets? Or is there some other motivation? Other than the RCD protected
socket you added, are there no other sockets in the room?
Perhaps you ought to be looking at the broader picture, and changing
your system to include RCD protection for *all* the sockets in your
house - especially those that may be used to power appliances used
outside. This would need to be done at the consumer unit end of things.
Grafting on individualy protected sockets does sound like a hard way to
do it.
If you have no plans to ever use the immersion heater, then you could
simply disconnect it and re-designate the circuit. If you changed its
MCB for a 30mA trip 20A type B RCBO, then you could use that cable as a
radial circuit to supply a number of sockets as and where you need them.
These sockets would then all have RCD protection. Perhaps you might be
better off looking at getting the CU changed for a split load unit so
you could have all socket circuite RCD protected.
bob watkinson
Mark, me old son, everything about your postings scream at me that you
haven't got a scoobydo what you're talking about. You even dismiss with
contempt the advice freely given by A R Wadsworth, a qualified sparky
who is telling you succinctly how the job should be done. Do yourself a
favour and get in a proper sparky. You really have no idea just how
little you know.
Mark
Bob me old mate. As it happens I have a degree in electronics
engineering so I do feel I'm qualified to go 'poking about' in my
consumer unit. Just that I never bothered to find out how an RCD
works. Now I've located a circuit diagram of the inside of an RCD it
is clear to me that it will only protect loads connected downstream of
it. In the course of my work I have frequently suffered the cowboy
bodges of so called 'proper' sparkies in the factory environment where
H&S is paramount. In fact one nearly killed me when he assured me he
had isolated a circuit and it turned out he hadn't. So I tend to have
a healthy disrespect for 'proper' sparkies until they have
demonstrated the quality of their work to me. I also assume it was a
'proper' sparky who wired my house in the first place (new build) and
didn't tighten the screws in the back of two sockets resulting in them
burning out when first used with a high load. So please don't lecture
me about using professionals. I imagine many of the posters in this
group are into DIY, not because they want to save money or derive
pleasure from it, but because they want the job done right the first
time around.
Regarding the advice from A R Wadsworth, it was worth what I paid for
it. He is typical of many in newsgroups who seek to get on their
soapbox and berate and patronise posters rather than try to educate
and impart knowledge. Had someone simply answered my question and
explained how an RCD worked then it would have been job done.
Andy Dingley
To give you the simple answer you obviously want, then No!
Years ago, voltage-activated ELCBs were sometimes used. In some cases,
these might have triggered owing to a fault current in the way you
describe (but not to an extent you'd want to rely on).
Today though, we use RCCDs that work by detecting currents and they
will only do it for "downstream" devices.
bob watkinson
consumer unit.
Perhaps, but you are the most dangerous type of bodger there is. The
type who actually believe their knowledge is greater than a specialist.
On you go mate, you've torn up the regulations and don't care whether
or not you kill anyone. Why ask advice anyhow if you don't like the
answer?