Two fixtures from 12/3 romex? NEC question

JDS

Usenet Archive
Joined
Apr 7, 2005
Messages
27
Reaction score
0
Hi all,

I have a question about NEC regarding a situation I discovered in my house. I was adding a new circuit for a shop light in my garage when I came across some 12/3 Romex that was powering some fixtures in the ADU that is attached to it. There are two lights in the bathroom of the ADU, one vanity light and one fan/light combo. They were running from a run of 12/3 romex, but wired in such a way that each had its own hot cable (one black, one red) and were sharing a common ground and neutral. Each had a 15A breaker back in the box. My first question is, is this allowable under NEC? Since it seems overkill to have a whole 15A breaker for each light, I was wondering if I could just run each hot (black and red) from the same 15A breaker? Or should I just rip it all out and run them in series on some 12/2 Romex? I have a little quick reference book about NEC but it doesn't mention anything about this.

Big 8' shop lights turned out great though!

Thanks!

-JDS
 

Chris Lewis

Usenet Archive
Joined
Jul 17, 2000
Messages
1,973
Reaction score
0
According to JDS said:
I have a question about NEC regarding a situation I discovered in my house. I was adding a new circuit for a shop light in my garage when I came across some 12/3 Romex that was powering some fixtures in the ADU that is attached to it. There are two lights in the bathroom of the ADU, one vanity light and one fan/light combo. They were running from a run of 12/3 romex, but wired in such a way that each had its own hot cable (one black, one red) and were sharing a common ground and neutral. Each had a 15A breaker back in the box. My first question is, is this allowable under NEC?
Look for "Multi-wire branch circuit". Yes, they're legal. I prefer that the breakers be tie-barred, but in this case they don't need to be under NEC. (Under CEC they do).
Since it seems overkill to have a
whole 15A breaker for each light, I was wondering if I could just run each hot (black and red) from the same 15A breaker?
You could.
 

Toller

Usenet Archive
Joined
Mar 19, 2003
Messages
1,975
Reaction score
0
Chris Lewis said:
Look for "Multi-wire branch circuit". Yes, they're legal. I prefer that the breakers be tie-barred, but in this case they don't need to be under NEC. (Under CEC they do).

You could.
You could if the breaker is rated for two wires; otherwise you can pigtail them; but that is ugly. Only problem might be that someone in the future might assume it was a properly wired multiwire circuit.
 

SQLit

Usenet Archive
Joined
Nov 4, 2003
Messages
2,237
Reaction score
0
JDS said:
Hi all,

I have a question about NEC regarding a situation I discovered in my house. I was adding a new circuit for a shop light in my garage when I came across some 12/3 Romex that was powering some fixtures in the ADU that is attached to it. There are two lights in the bathroom of the ADU, one vanity light and one fan/light combo. They were running from a run of 12/3 romex, but wired in such a way that each had its own hot cable (one black, one red) and were sharing a common ground and neutral. Each had a 15A breaker back in the box. My first question is, is this allowable under NEC? Since it seems overkill to have a whole 15A breaker for each light, I was wondering if I could just run each hot (black and red) from the same 15A breaker? Or should I just rip it all out and run them in series on some 12/2 Romex? I have a little quick reference book about NEC but it doesn't mention anything about this.

Big 8' shop lights turned out great though!

Thanks!

-JDS
What is ADU?

If the fan light has a heat lamp in it, a separate circuit might be a good idea.
 

Andy Hill

Usenet Archive
Joined
May 6, 2003
Messages
254
Reaction score
0
JDS said:
I have a question about NEC regarding a situation I discovered in my house. I was adding a new circuit for a shop light in my garage when I came across some 12/3 Romex that was powering some fixtures in the ADU that is attached to it. There are two lights in the bathroom of the ADU, one vanity light and one fan/light combo. They were running from a run of 12/3 romex, but wired in such a way that each had its own hot cable (one black, one red) and were sharing a common ground and neutral. Each had a 15A breaker back in the box. My first question is, is this allowable under NEC? Since it seems overkill to have a whole 15A breaker for each light, I was wondering if I could just run each hot (black and red) from the same 15A breaker? Or should I just rip it all out and run them in series on some 12/2 Romex? I have a little quick reference book about NEC but it doesn't mention anything about this.
If the two 15A breakers are on opposite sides of the incoming 240 (an Edison circuit), then the current wiring is OK.

What you suggest is OK from a safety standpoint, but why? The current setup works and is code (I'm assuming). Tying the red/black together is going to create a potentially confusing situation, since the usual assumption is "1 conductor = 1 breaker capacity", and you're violating that assumption.
 

Chip C

Usenet Archive
Joined
Nov 25, 2003
Messages
220
Reaction score
0
JDS said:
Hi all,

I have a question about NEC regarding a situation I discovered in my house. I was adding a new circuit for a shop light in my garage when I came across some 12/3 Romex that was powering some fixtures in the ADU that is attached to it. There are two lights in the bathroom of the ADU, one vanity light and one fan/light combo. They were running from a run of 12/3 romex, but wired in such a way that each had its own hot cable (one black, one red) and were sharing a common ground and neutral. Each had a 15A breaker back in the box. My first question is, is this allowable under NEC? Since it seems overkill to have a whole 15A breaker for each light, I was wondering if I could just run each hot (black and red) from the same 15A breaker? Or should I just rip it all out and run them in series on some 12/2 Romex? I have a little quick reference book about NEC but it doesn't mention anything about this.

Big 8' shop lights turned out great though!

Thanks!

-JDS
You must make sure that the two breakers are on opposite legs in the panel; in most panels this is the case if the breakers are next to each other. This makes sure the current cancels out in the neutral instead of adding.

It does seem like overkill, doesn't it. To have the bathroom *outlet* on its own breaker would make more sense.

Chip C
Toronto
 

JDS

Usenet Archive
Joined
Apr 7, 2005
Messages
27
Reaction score
0
Hey all, sorry about the direct replies. I meant to reply to the group.

Thanks for all the help.

-JDS
 

RBM

Usenet Archive
Joined
Nov 22, 2004
Messages
5,194
Reaction score
0
The multiwire branch circuit is legal, however your question rewarding the bathroom wiring itself depends on when it was wired. As codes change, wiring methods do as well. Current NEC allows two ways to wire bathrooms. One way, all bathroom outlets can share a common 20 amp circuit. The lights in the bathrooms can be on any other circuit. The second method is that all lights and outlets in each bathroom be on dedicated twenty amp circuits.
 

JDS

Usenet Archive
Joined
Apr 7, 2005
Messages
27
Reaction score
0
RBM said:
The multiwire branch circuit is legal, however your question rewarding the bathroom wiring itself depends on when it was wired. As codes change, wiring methods do as well. Current NEC allows two ways to wire bathrooms. One way, all bathroom outlets can share a common 20 amp circuit. The lights in the bathrooms can be on any other circuit. The second method is that all lights and outlets in each bathroom be on dedicated twenty amp circuits.
Currently the ADU wall outlets are all on one circuit, this includes the single outlet in the bathroom, so I am in violation right there I guess. From what I understand about code when someone renovates is that if I start messing around with it, I need to bring it all up to code. So maybe I should run a dedicate 20A circuit to the bathroom for the light, light/fan and outlet. Better bust out my fish tape!

-JDS
 

RBM

Usenet Archive
Joined
Nov 22, 2004
Messages
5,194
Reaction score
0
In GE panels they make half sized double pole breakers that connect to "T" slots, so it may be hard to tell. If you have a volt meter test across the red and black of the multi wire circuit and you should read 240 volts. If the meter reads nothing, it's wrong
 

Chris Lewis

Usenet Archive
Joined
Jul 17, 2000
Messages
1,973
Reaction score
0
You could if the breaker is rated for two wires; otherwise you can pigtail them; but that is ugly.
Most of the breakers I've worked with are rated for two. The ones with metal plate "washers" that clamp the wire would all be.

I should point out that "workmanship rules" (ie: comments in Knight) say "only one wire in the panel per breaker".

Yeah, pigtailing is ugly. I hates it ;-)
Only problem might be that someone in the future
might assume it was a properly wired multiwire circuit.
If you were going by what you saw in boxes _other_ than the panel, you'd assume the red to be part of a switch circuit (ie: three way, or certain other arrangements such as switched outlets). As such, I don't think there's likely to be an issue. I don't think the NEC/CEC cares. It might be more of a "workmanship" issue, but I don't think you'd get much resistance from an inspector on rearranging an _existing_ circuit.

In other words, you'd be okay with reworking existing wiring, but you shouldn't do "new" this way.
 

JDS

Usenet Archive
Joined
Apr 7, 2005
Messages
27
Reaction score
0
HorneTD said:
Do yourself a favor and run a new twenty ampere multi wire branch (Edison) circuit to the bath room. One leg will be the receptacle the other will be the bathroom heater. One eighteen hundred watt hair dryer is the entire ampacity of a fifteen ampere circuit. Even an electric tooth brush recharger would be enough additional load to trip a fifteen ampere circuit breaker. One you get the heater and plug of of the other circuit the light bulbs probably won't be enough to worry about.
Great idea! I can just rewire the existing wire and leave it in place. Put the lights and fan on the on leg and the plug on the other.

-JDS
 

Ask a Question

Want to reply to this thread or ask your own question?

You'll need to choose a username for the site, which only take a couple of moments. After that, you can post your question and our members will help you out.

Ask a Question

Members online

No members online now.

Forum statistics

Threads
144,906
Messages
1,592,100
Members
59,482
Latest member
lisac

Latest Threads

Top