Sweating large diameter copper pipe

Ken (archive)

Usenet Archive
Joined
Jan 3, 2000
Messages
807
Reaction score
0
We are in the middle of renovating a kitchen and bathroom. House was built in 1925, and kitchen pantry was converted to a bathroom I'm guessing in the 1950's. Current plumbing vent for the bathroom is 2" copper run on the exterior wall of the house. This vent will be moved into the wall cavity. (Already have the walls ripped out and holes in top plates drilled.) Hired plumber will be doing most of the work.

I'd like to reuse the current copper vent pipe inside the wall. I have no sound reasons for wanting to reuse the pipe other than I just like the idea of reusing old materials rather than always buying new, even if it adds to the cost of the job. We'll be asking the plumber about this, and I anticipate that his answer will be that it is way easier and cheaper to just run new PVC inside the wall than trying to clean up the pipe enough to sweat new couplings on as sections of the pipe are stuffed up the wall cavity.

Also, current waste pipe for the toilet is 3" (I think) copper. This had to be cut in one place as part of the renovation, so it would only take one coupling to reconnect the existing waste line to the new stuff.

So my question is, how hard is it to sweat a 2"+ diameter copper pipe? I've done plenty of 1/2" and 3/4", so I know how easy it is to do that, but does it become exponentially more difficult to sweat larger diameters? Is the plumber going to run screaming from our house if we ask him to do this? I assume he will want to just rip everything out and re-run PVC, so should we let him do this?

Thanks for any insight anyone can give me.

Ken
 

trader4

Usenet Archive
Joined
Dec 7, 2004
Messages
10,942
Reaction score
0
Any real plumber will have a torch that can easily solder 2" copper pipe. The real issues are how accessible it all is, how easy it is to get to the right spots to cut/solder it, and how much harder or costly it will be to do that instead of going with ABS
 

SQLit

Usenet Archive
Joined
Nov 4, 2003
Messages
2,237
Reaction score
0
Ken said:
We are in the middle of renovating a kitchen and bathroom. House was built in 1925, and kitchen pantry was converted to a bathroom I'm guessing in the 1950's. Current plumbing vent for the bathroom is 2" copper run on the exterior wall of the house. This vent will be moved into the wall cavity. (Already have the walls ripped out and holes in top plates drilled.) Hired plumber will be doing most of the work.

I'd like to reuse the current copper vent pipe inside the wall. I have no sound reasons for wanting to reuse the pipe other than I just like the idea of reusing old materials rather than always buying new, even if it adds to the cost of the job. We'll be asking the plumber about this, and I anticipate that his answer will be that it is way easier and cheaper to just run new PVC inside the wall than trying to clean up the pipe enough to sweat new couplings on as sections of the pipe are stuffed up the wall cavity.

Also, current waste pipe for the toilet is 3" (I think) copper. This had to be cut in one place as part of the renovation, so it would only take one coupling to reconnect the existing waste line to the new stuff.

So my question is, how hard is it to sweat a 2"+ diameter copper pipe? I've done plenty of 1/2" and 3/4", so I know how easy it is to do that, but does it become exponentially more difficult to sweat larger diameters? Is the plumber going to run screaming from our house if we ask him to do this? I assume he will want to just rip everything out and re-run PVC, so should we let him do this?

Thanks for any insight anyone can give me.

Ken
With a big "turbo torch" it is done daily. The average plumber may not have such a tool. Never seen one at a rental yard.

Last one I saw the flame end was 4 inches in diameter and they used dual gasses. Oxy and Acetylene. Took a skilled journeyman about 30 minutes a joint. No flammable materials anywhere near.

Since this is for a vent I would think about a "no hub" connection.
 
Joined
May 15, 2005
Messages
70
Reaction score
0
Glad this post is about plumbing because the last answer is as full of shit as any sewer i have ever seen. No turbo torch, no oxy assist feed. Average plumber will have a BTank that will handle job, prob is the labor to clean the couplings off old solder. Average joint only needs a minute to heat.
 

gfretwell

Usenet Archive
Joined
Mar 7, 2005
Messages
1,215
Reaction score
0
Any real plumber will have a torch that can easily solder 2" copper pipe.
Around here it is hard to find a plumber who knows anything but "pasting plastic". I think most of them get into the trade because they like the smell of the glue
 

trader4

Usenet Archive
Joined
Dec 7, 2004
Messages
10,942
Reaction score
0
"Glad this post is about plumbing because the last answer is as full of shit as any sewer i have ever seen. No turbo torch, no oxy assist feed. Average plumber will have a BTank that will handle job, prob is the labor to clean the couplings off old solder. Average joint only needs a minute to heat."

I got a good laugh out of it too. Turbo torch with 4 inch diameter flame and 30 mins a joint to solder a 2" copper pipe. LOL He must have been smoking a joint and watching a shuttle launch!
 

Robert Allison

Usenet Archive
Joined
Feb 22, 2003
Messages
853
Reaction score
0
SQLit said:
With a big "turbo torch" it is done daily. The average plumber may not have such a tool. Never seen one at a rental yard.

Last one I saw the flame end was 4 inches in diameter and they used dual gasses. Oxy and Acetylene. Took a skilled journeyman about 30 minutes a joint. No flammable materials anywhere near.

Since this is for a vent I would think about a "no hub" connection.
That had to have been on a government job. Were there 5 or 6 "inspectors" standing around watching and a guy with a fire extinquisher?
 

Stormin Mormon

Usenet Archive
Joined
Aug 10, 2002
Messages
21,983
Reaction score
0
When I used to do a lot more heating and AC installs, the boss and I used to work together on solder joints like that. It was a sight to behold. Two bespectacled Mormons, with ball caps, clip on sunglasses, pockets full of pens. Two mapp torches, and two rolls of solder. We'd talk about anything and everything while the pipe heated. Hit it with solder, wipe it off, and get on to the next one. That was the good life. Never ridicule nerds, they are the only ones who can fix your furnace and AC.

--

Christopher A. Young
Learn more about Jesus
www.lds.org
www.mormons.com

We are in the middle of renovating a kitchen and bathroom. House was built in 1925, and kitchen pantry was converted to a bathroom I'm guessing in the 1950's. Current plumbing vent for the bathroom is 2" copper run on the exterior wall of the house. This vent will be moved into the wall cavity. (Already have the walls ripped out and holes in top plates drilled.) Hired plumber will be doing most of the work.

I'd like to reuse the current copper vent pipe inside the wall. I have no sound reasons for wanting to reuse the pipe other than I just like the idea of reusing old materials rather than always buying new, even if it adds to the cost of the job. We'll be asking the plumber about this, and I anticipate that his answer will be that it is way easier and cheaper to just run new PVC inside the wall than trying to clean up the pipe enough to sweat new couplings on as sections of the pipe are stuffed up the wall cavity.

Also, current waste pipe for the toilet is 3" (I think) copper. This had to be cut in one place as part of the renovation, so it would only take one coupling to reconnect the existing waste line to the new stuff.

So my question is, how hard is it to sweat a 2"+ diameter copper pipe? I've done plenty of 1/2" and 3/4", so I know how easy it is to do that, but does it become exponentially more difficult to sweat larger diameters? Is the plumber going to run screaming from our house if we ask him to do this? I assume he will want to just rip everything out and re-run PVC, so should we let him do this?

Thanks for any insight anyone can give me.

Ken
 

Edwin Pawlowski

Usenet Archive
Joined
Sep 25, 2001
Messages
8,269
Reaction score
0
SQLit said:
Last one I saw the flame end was 4 inches in diameter and they used dual gasses. Oxy and Acetylene. Took a skilled journeyman about 30 minutes a joint. No flammable materials anywhere near.
If it took 30 minutes a joint, he was far from a skilled anything. Even a hack can to that type of joint in just a couple of minutes.
 

DanG

Usenet Archive
Joined
Nov 9, 2003
Messages
1,960
Reaction score
0
We have done exactly this quite a few times. I suspect he saw a repair job on large, heavy copper water line. We have used two rosebuds (there is your 4" diameter flame) to get the moisture out of the line. To get the copper up to solder temperature we certainly do use oxy acetylene on 4" heavy wall copper. A B bottle will work, but I think you would be hard pressed with a typical propane torch. The OP is talking about soldering light weight 2" and I agree that soldering dry thinwall pipe is quite doable with a good propane torch.

(top posted for your convenience)
^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^
Keep the whole world singing . . . .
DanG (remove the sevens)
 

Duane Bozarth

Usenet Archive
Joined
Jan 2, 2002
Messages
1,556
Reaction score
0
Edwin said:
If it took 30 minutes a joint, he was far from a skilled anything. Even a hack can to that type of joint in just a couple of minutes.
Maybe it was standing full of liquid H or something so it was hard to heat! :)
 

Duane Bozarth

Usenet Archive
Joined
Jan 2, 2002
Messages
1,556
Reaction score
0
DanG said:
We have done exactly this quite a few times. I suspect he saw a repair job on large, heavy copper water line. We have used two rosebuds (there is your 4" diameter flame) to get the moisture out of the line. To get the copper up to solder temperature we certainly do use oxy acetylene on 4" heavy wall copper. A B bottle will work, but I think you would be hard pressed with a typical propane torch.
....

That was my read of what he must have seen, too....
 

Chris Lewis

Usenet Archive
Joined
Jul 17, 2000
Messages
1,973
Reaction score
0
According to Ken said:
So my question is, how hard is it to sweat a 2"+ diameter copper pipe? I've done plenty of 1/2" and 3/4", so I know how easy it is to do that, but does it become exponentially more difficult to sweat larger diameters? Is the plumber going to run screaming from our house if we ask him to do this? I assume he will want to just rip everything out and re-run PVC, so should we let him do this?
In a job I once worked on, the (master) plumber had to fish a long run 2" copper _through_ the floor joists. Meaning he had to solder the pipe between each and every joist.

[This was half of a duplex - in "commercial" work, you have to use copper even for DWV. Here at least... He did quite a bit of other large-diameter copper too.]

He was using an acetylene torch without oxygen. A small tank with a hose to the torch.

It didn't take him very long to do 20ish connections.

Not a big deal - to him at least ;-)

You might find it relatively difficult to do yourself with a standard cheapie propane torch, but if you used MAPP/MPS cylinder instead, it should be considerably easier. I use MPS gas myself now, because it's considerably quicker - especially if I have to solder something outdoors in high winds ;-)
 

Ask a Question

Want to reply to this thread or ask your own question?

You'll need to choose a username for the site, which only take a couple of moments. After that, you can post your question and our members will help you out.

Ask a Question

Similar Threads


Members online

No members online now.

Forum statistics

Threads
144,907
Messages
1,592,101
Members
59,482
Latest member
lisac

Latest Threads

Top