replacing Schrader valves


S

sidwelle

Background: Failing AC system in western suburb of Chicago. Unit is 22 years old, Carrier 2 ton w/gas furnace 70k btu.

I had a tech out today to look at my AC and give me an estimate on replacing the system with a high-efficiency system and be eligible for gov. rebate.
He gave me several options, but the last option was that he could probably fix the existing unit by just replacing the Schrader valves for $2-250. He said that if the unit is freezing up that it is still operational and had some life left in it.

What is the opinion and/or success rate on replacing the Schrader valves.

Thanks
 
Ad

Advertisements

N

No Body

What is the opinion and/or success rate on replacing the Schrader valves.
If it's leaking Schrader valves, the success is nearly 100%

They even make a tool for replacing them.

Here's the tool:

<http://www.homedepot.com/p/t/203568882?productId=203568882&storeId=10051\
&langId=-1&catalogId=10053&ci_sku=203568882&ci_src=17588969\
&cm_mmc=shopping-_-googleads-_-pla-_-203568882&ci_gpa=pla#.Ug8KB006OOE>

or

<http://www.johnstonesupply.com/storefront/product-view.ep?pID=H24-611>

These allow you to remove the valve core, put in a new one.. and you hardly
loose any refrigerant.

But.. if it's just a slow leak.. and the unit is on it's last legs, a
"cap" over the Schrader valve will seal the valve, after the unit
has been re-charged.. and the cap has a rubber gasket which will
keep the unit from leaking.

It will be hard to service, in that, when you open the cap you will
loose a small amount of refrigerant.. but, unless the valve is
completely shot, they usually just leak a little.. (In fact
every one of them I've ever seen, leaked a little.. it's just
"does it leak so much that you can't get a cap on it in time
to preserve the charge.
 
K

Ken

No said:
If it's leaking Schrader valves, the success is nearly 100%

They even make a tool for replacing them.

Here's the tool:

<http://www.homedepot.com/p/t/203568882?productId=203568882&storeId=10051\
&langId=-1&catalogId=10053&ci_sku=203568882&ci_src=17588969\
&cm_mmc=shopping-_-googleads-_-pla-_-203568882&ci_gpa=pla#.Ug8KB006OOE>

or

<http://www.johnstonesupply.com/storefront/product-view.ep?pID=H24-611>

These allow you to remove the valve core, put in a new one.. and you hardly
loose any refrigerant.

But.. if it's just a slow leak.. and the unit is on it's last legs, a
"cap" over the Schrader valve will seal the valve, after the unit
has been re-charged.. and the cap has a rubber gasket which will
keep the unit from leaking.

It will be hard to service, in that, when you open the cap you will
loose a small amount of refrigerant.. but, unless the valve is
completely shot, they usually just leak a little.. (In fact
every one of them I've ever seen, leaked a little.. it's just
"does it leak so much that you can't get a cap on it in time
to preserve the charge.
Your suggestion of using a cap with a rubber O-ring is right on. I paid
a serviceman hundreds of dollars to find a leak on my unit, only to
discover the leak was at the Schrader valve. It was solved by the cap
and held a charge for years after installing it. To say that I was
upset with the technician's performance would be the understatement of
the year. Yes he did have a sniffer for detecting Freon, and one would
have thought that would have been the first place he would have used it.
It is incidents like this that make people suspicious of servicemen
for their HVAC units.
 
T

Tony944

Ken said:
Your suggestion of using a cap with a rubber O-ring is right on. I paid a
serviceman hundreds of dollars to find a leak on my unit, only to discover
the leak was at the Schrader valve. It was solved by the cap and held a
charge for years after installing it. To say that I was upset with the
technician's performance would be the understatement of the year. Yes he
did have a sniffer for detecting Freon, and one would have thought that
would have been the first place he would have used it. It is incidents
like this that make people suspicious of servicemen for their HVAC units.
There are solid brass bonnets made even if Schrader valve leaks,

The solid bonnet will seal unless there are damaged face or treads.

However one should always check process valve once service is completed!
 
N

No Body

Your suggestion of using a cap with a rubber O-ring is right on. I paid
a serviceman hundreds of dollars to find a leak on my unit, only to
discover the leak was at the Schrader valve. It was solved by the cap
and held a charge for years after installing it. To say that I was
upset with the technician's performance would be the understatement of
the year. Yes he did have a sniffer for detecting Freon, and one would
have thought that would have been the first place he would have used it.
It is incidents like this that make people suspicious of servicemen
for their HVAC units.
Oh.. I dunno...

Everybody has their "priority list" based on their own experience with
various types of systems.

He's got a truck load of gear, and probably several years of
experience.. and he probably searches in an order that he has
found has worked in the past.

Some machines are more prone to particular types of failures than
others.

Usually, when you pull the service caps off you get a quick
whiff of freon.. they all leak a bit.

Now.. if somebody serviced the machine and didn't put the caps back,
then that's the first place I'd look! And.. it's one of the first
places the tech goes, 'cus he needs to hook up his gage set to see
what's going on.

Usually all he's got is a vague "It doesn't cool well any more, or
it freezes up".. as a symptom.

He's got to start someplace.

It's about like the computer tech that shows up, to a problem that
has baffled folks for weeks.

He walks in, checks a couple of things.. gives the machine a swift
kick.. and hands them a bill for $10,000.00..

They all balk at the bill.

So.. he re-writes the bill.

Diagnosis. $200.00
Application of corrective action. $10.00
Knowing where and how hard to kick $10,000.00

And they paid him the $10,210.00!
 
K

Ken

No said:
Oh.. I dunno...

Everybody has their "priority list" based on their own experience with
various types of systems.

He's got a truck load of gear, and probably several years of
experience.. and he probably searches in an order that he has
found has worked in the past.

Some machines are more prone to particular types of failures than
others.

Usually, when you pull the service caps off you get a quick
whiff of freon.. they all leak a bit.

Now.. if somebody serviced the machine and didn't put the caps back,
then that's the first place I'd look! And.. it's one of the first
places the tech goes, 'cus he needs to hook up his gage set to see
what's going on.

Usually all he's got is a vague "It doesn't cool well any more, or
it freezes up".. as a symptom.

He's got to start someplace.

It's about like the computer tech that shows up, to a problem that
has baffled folks for weeks.

He walks in, checks a couple of things.. gives the machine a swift
kick.. and hands them a bill for $10,000.00..

They all balk at the bill.

So.. he re-writes the bill.

Diagnosis. $200.00
Application of corrective action. $10.00
Knowing where and how hard to kick $10,000.00

And they paid him the $10,210.00!
I can appreciate your explanation, but after two years of trouble
shooting, one would think the first place a person would look for a leak
is where the Freon is inserted. I could tell you many more stories
about HVAC techs, but I am sure you do not want to hear them.
 
Ad

Advertisements

S

sidwelle

The tech also started to talk about the fact that some times the leak is inthe copper lines running under the slab, and if so you have to cut a lot of concrete to install new lines. He recovered and stated that the leak is almost always at the Schrader valves. Do you every find that the copper tubes fail ?

What about cleaning the tubes ? Some techs talking about cleaning and others talk about just evacuating them does a better job ?

Thanks
 
N

No Body

I can appreciate your explanation, but after two years of trouble
shooting, one would think the first place a person would look for a leak
is where the Freon is inserted. I could tell you many more stories
about HVAC techs, but I am sure you do not want to hear them.
There are hacks in every profession.. and some outright crooks sprinkled
in for good measure.

A schrader valve under a good cap wouldn't be too high on my list, because
the cap would stop a leak there.. and because, since every schrader valve
leaks a tiny amount.. sniffing right after you pull the cap will almost
always show a whiff.. but that's only because the small amount that leaks
by the valve is trapped under the cap.

And when a service hose is on the valve, it's "open". So... getting some
right after you pull the hose is a high possibility.. but it still doesn't
indicate the source of a "leak".

Still... two years is a bit long.
 
N

No Body

The tech also started to talk about the fact that some times the leak is in the copper lines running under the
slab, and if so you have to cut a lot of concrete to install new lines. He recovered and stated that the leak
is almost always at the Schrader valves. Do you every find that the copper tubes fail ?
Not often.. especially if they are installed correctly.

That said.. a copper tube "rattling" against a hard edge can fail.
What about cleaning the tubes ? Some techs talking about cleaning and others talk about just
evacuating them does a better job ?
If a hermetic compressor has burned out, cleaning is a good idea.

It usually leaves "waste products" from the burnout all over..and some
of them are corrosive.
 
T

The Daring Dufas

The tech also started to talk about the fact that some times the leak
is in the copper lines running under the slab, and if so you have to
cut a lot of concrete to install new lines. He recovered and stated
that the leak is almost always at the Schrader valves. Do you every
find that the copper tubes fail ?

What about cleaning the tubes ? Some techs talking about cleaning and
others talk about just evacuating them does a better job ?

Thanks
I use a cleaning fluid sucked in with a vacuum pump then blown out with
dry nitrogen. Back in the good old days you could use R11 to clean out a
system but these days we must protect the cute fuzzy little ozones.
After cleaning out the condenser, evaporator and line set, I do a triple
vacuum on the system after determining there are no leaks then recharge
it and start it up. If it's done right you'll never have a failure due
to contamination. Of course make sure there is enough oil in the system. ^_^

TDD
 
T

The Daring Dufas

I use a cleaning fluid sucked in with a vacuum pump then blown out with
dry nitrogen. Back in the good old days you could use R11 to clean out a
system but these days we must protect the cute fuzzy little ozones.
After cleaning out the condenser, evaporator and line set, I do a triple
vacuum on the system after determining there are no leaks then recharge
it and start it up. If it's done right you'll never have a failure due
to contamination. Of course make sure there is enough oil in the system.
^_^

TDD
Oh hell, I forgot a small bottle of acid neutralized added to the
compressor oil as insurance. It will neutralize any acid that may have
been trapped in the system. ^_^

TDD
 
Ad

Advertisements

T

Tony Hwang

Ken said:
I can appreciate your explanation, but after two years of trouble
shooting, one would think the first place a person would look for a leak
is where the Freon is inserted. I could tell you many more stories
about HVAC techs, but I am sure you do not want to hear them.
Hi,
I spent all my working career as a support specialist for things field
techs couldn't figure out or handle(not in HVAC field). Years of dealing
with them worst techs are those who approach problems based on past
experience rather than looking at it as brand new first time seen
problem. This type of techs never improve themselves. Waste lots of time
and cause lots of trouble for other fellow techs including those like me.
 
N

No Body

Hi,
I spent all my working career as a support specialist for things field
techs couldn't figure out or handle(not in HVAC field). Years of dealing
with them worst techs are those who approach problems based on past
experience rather than looking at it as brand new first time seen
problem. This type of techs never improve themselves. Waste lots of time
and cause lots of trouble for other fellow techs including those like me.
A good field service tech is a mix of skills... Observation being the most
key.

And fresh eyes always help.. When you have been looking at a problem too
long you can get into the mode of "I've already checked that, it can't be..."

Some techs can "cookbook" themselves thru a problem, and, when they have
replaced enough parts, the system is functional again.. but often there
are a pile of good parts that have been replaced, needlessly.
 
P

PaxPerPoten

The tech also started to talk about the fact that some times the leak is in the copper lines running under the slab, and if so you have to cut a lot of concrete to install new lines. He recovered and stated that the leak is almost always at the Schrader valves. Do you every find that the copper tubes fail ?

What about cleaning the tubes ? Some techs talking about cleaning and others talk about just evacuating them does a better job ?

Thanks
If those lines are touching that concrete slab...you may also have a
flash gas problem. cleaning the fins on the condenser and the evaporator
is just standard good annual(or more) practices. Perhaps it is time for
you to renew that system anyway. The cost of R22 and its availability is
rapidly putting it on the endangered species list. The new cooling gases
and the higher efficiency systems may well be your best bet.
 
P

PaxPerPoten

Diagnosing correctly is overrated, just change out parts. You make more
money that way.
Bull! Jest sell-um a new unit and maintenance warranty.;-p
 
Joined
Apr 2, 2015
Messages
76
Reaction score
4
I am not a HVAC tech , just a DIY'er that has been in construction over 30 years .

I consider replacing Schrader valves as preventive maintenance . Bought the core remover tool years ago . Coat the new Schrader valve with refrigeration oil before you install it .

God bless
Wyr
 