Greetings,

I would like to feed two main lug only subpanels from the same 100A breaker and the same 2 AGW Al SEU wire. I understand how the subpanel at the "end of chain" should be terminated but I am unsure of the "standard" way to attach the center subpanel.

Diagram
200A Main <---2 awg al---> 100A Sub <---2 awg al---> 100A Sub

Thank you all very much in advance.

William
 

RBM

Usenet Archive
Joined
Nov 22, 2004
Messages
5,194
Reaction score
0
Without knowing the proximity of the sub panels to one another, one method would be to run the feeder into a screw cover box with individual cables out to each panel. Keep in mind, unless these panels are for 240 volt only (no neutral) you'll need to use SER (four wire) for single phase 120/240
 

deans

Usenet Archive
Joined
Jun 10, 2005
Messages
391
Reaction score
0
Additional Information
I am sorry -- that was a typo -- I used SER.
The panels are 25' and 50' away from the main panel.

Additional Questions Raised
I looked at table 314.16(A/B) but was unable to locate the size box I would need for 10 2AWG wires. How many in^3 does each 2 AWG wire require? Is there another calculation mechanism I need to use?
 

RBM

Usenet Archive
Joined
Nov 22, 2004
Messages
5,194
Reaction score
0
Don't have a code book handy, but I believe you can't fill more than forty percent. Personally, when it comes to boxes of any type, I like the biggest I can fit rather than the smallest that's permissible
 

John Grabowski

Usenet Archive
Joined
Jul 5, 2003
Messages
2,104
Reaction score
0
William, Check out article 314.28 (2005 NEC) for additional information on sizing your junction box. Also check 338.24 for bending requirements of service entrance cable.

John Grabowski
http://www.mrelectrician.tv
 

zxcvbob

Usenet Archive
Joined
Jul 10, 2001
Messages
1,274
Reaction score
0
Greetings,

I would like to feed two main lug only subpanels from the same 100A breaker and the same 2 AGW Al [SER] wire. I understand how the subpanel at the "end of chain" should be terminated but I am unsure of the "standard" way to attach the center subpanel.

Diagram
200A Main <---2 awg al---> 100A Sub <---2 awg al---> 100A Sub

Thank you all very much in advance.

William
I don't know how it's *supposed* to be done, but I would look for a center panel with 2 sets of main lugs or an optional feedthru lug kit.

The other way I might try to do it is: Cut the wires at the first box and terminate normally, but strip an extra inch or 2 of insulation off the wires, and maybe leave a little extra slack. Then use big aluminum split bolt connectors (and black goop) to connect the outgoing cable to the exposed bare conductors of the incoming cable, then wrap with electrical tape as appropriate. (you won't need to wrap the grounding wire, obviously)

Best regards,
Bob
 

Ask a Question

Want to reply to this thread or ask your own question?

You'll need to choose a username for the site, which only take a couple of moments. After that, you can post your question and our members will help you out.

Ask a Question

Members online

No members online now.

Forum statistics

Threads
144,906
Messages
1,592,100
Members
59,482
Latest member
lisac

Latest Threads

Top