first: good group - i'm a lurker but learn a lot by reading!

i am purchasing a great hot tub from a co-worker for excellent price (he's upgrading). i'm moving it saturday to the back patio of my townhome, i'm sure everyone envys that job.

i have an electrician coming saturday evening, and am going to request he use the 220 power in the laundry room to hardwire the hot tub to. (my dryer is gas, so i don't use it), and the fuse box has two switches strictly for the dryer.

the basement outlet is right next to the patio, so pretty close,

but a hot tub dealer mention the outlet might be 30amp, and the hot tub is 50amp

should i be concerned about this? and is it a correctable problem, and at approx. what price?

thanks in advance, i appreciate it!
 

RBM

Usenet Archive
Joined
Nov 22, 2004
Messages
5,194
Reaction score
0
Ditto JohnH, with the possible exception: Some units have an integral GFCI device. The dryer circuit is definitely not useable
 

trader4

Usenet Archive
Joined
Dec 7, 2004
Messages
10,942
Reaction score
0
"You will need to run a 4 wire cable directly to the breaker box, connected to a proper GFCI breaker, through a cutoff switch. Anything else will be an unsafe rig. "

Why does it have to be a direct run? I don't know of any code or safety requirement that calls for this. As long as the wire is the appropriate size and he gets a GFCI and disconnect installed, I don't see anything wrong with eliminating the dryer outlet and starting the run from there. Of course, it's very likely the existing wire gauge isn't adequate anyway, but that's a different issue.
 

JohnH (archive)

Usenet Archive
Joined
Apr 9, 2005
Messages
133
Reaction score
0
"You will need to run a 4 wire cable directly to the breaker box, connected to a proper GFCI breaker, through a cutoff switch. Anything else will be an unsafe rig. "

Why does it have to be a direct run? I don't know of any code or safety requirement that calls for this. As long as the wire is the appropriate size and he gets a GFCI and disconnect installed, I don't see anything wrong with eliminating the dryer outlet and starting the run from there. Of course, it's very likely the existing wire gauge isn't adequate anyway, but that's a different issue.
You are correct; that will work IF the dryer outlet is removed and the wires have the proper ampacity and separate neutral and grounds.

It seems to me it'd just be simpler and cleaner to run a whole new line, unless he can save substantial money by starting the run from there. Perhaps it will be cheaper as 4 conductor #6 isn't cheap! ;)
 

James (archive)

Usenet Archive
Joined
May 28, 2000
Messages
584
Reaction score
0
my dryer outlet doesn't work anyway. it came up bad in my home inspection last year. (not sure if wiring is ok or not)

i'm mainly concerned about the 30/50 amp difference -- but if new wiring needs to originate from breaker box it's no problem. it's on the main floor of my townhome, and can drop the wires behind the wall into the ceiling of laundry room, then out to patio. (see below side view)

i guess i'm more concerned if the two breakers can accept the load of a hot tub - but it's 220, like a dryer, i'm guessing i'm ok?

thanks again for the responses! and don't worry i'm having an electrician do it, just want to get some knowledge first.

HOT TUB________________ BREAKER BOX ------- - MAIN FLOOR

__________DRYER OUTLET__________ ------------------- BASEMENT
 

trader4

Usenet Archive
Joined
Dec 7, 2004
Messages
10,942
Reaction score
0
james said:
my dryer outlet doesn't work anyway. it came up bad in my home inspection last year. (not sure if wiring is ok or not)

i'm mainly concerned about the 30/50 amp difference -- but if new wiring needs to originate from breaker box it's no problem. it's on the main floor of my townhome, and can drop the wires behind the wall into the ceiling of laundry room, then out to patio. (see below side view)

i guess i'm more concerned if the two breakers can accept the load of a hot tub - but it's 220, like a dryer, i'm guessing i'm ok?
What breakers are there won't matter. It sounds like what you will need is a 240V 50 amp GFCI. This will either go in as

1 - A new location in the service panel

2 - Replacing the existing breaker for the dryer, which is very likely not 50 Amp. The question for this method is whether it can even be done, as the wire run for the dryer may not be of sufficient gauge. Also, given that you have to take out the dryer outlet, put in some kind of appropriate junction box, etc, it might be easier and about the same cost to just make a new run.
 

Doug Miller

Usenet Archive
Joined
Sep 11, 2002
Messages
4,265
Reaction score
0
i guess i'm more concerned if the two breakers can accept the load of a hot tub - but it's 220, like a dryer, i'm guessing i'm ok?
No, not if the dryer circuit is 30A at 220V and the hot tub draws 50A at 220V.
 

Tom (archive)

Usenet Archive
Joined
Jul 1, 2000
Messages
1,217
Reaction score
0
And national code requires that the disconnect be _within sight_ of the pool/spa. If you wanna go by the NEC... Tom
 

Chris Lewis

Usenet Archive
Joined
Jul 17, 2000
Messages
1,973
Reaction score
0
True enough!
We can tell him what he needs (roughly ;-) if he can give us the plate amperage rating off the spa, the ampacity of the dryer breakers, whether the dryer circuit is 3 or 4 wire, and whether the spa needs 3 or 4 wire.

Even if the dryer circuit is of adequate ampacity/wire count for the spa, he'll probably need to install a GFCI breaker (unless there's already one built into the spa).
 

James (archive)

Usenet Archive
Joined
May 28, 2000
Messages
584
Reaction score
0
thanks for the responses. i'll know tomorrow evening when the electrician comes, but this helps me get an idea!

he's a good electrician - friend and knowledgeable
 

James (archive)

Usenet Archive
Joined
May 28, 2000
Messages
584
Reaction score
0
follow up - complete!

well we brought the enormous hot tub into my back patio, (through city fence which i repaired. was 7.5 x 7.5 by about 4' high - a nice size 5-7 person spa. also had to rotate it 90, not only that but raining steadily here in Denver all morning, but I didn't mind that, as the park my place backs up to was empty and no cars around - made backing in the trailer easier.

the electrical company, who i've used before, came saturday afternoon, same day - and rain a new four wire connect straight from my breaker box (see my above diagram), out to the patio. i have a disconnect box next to the AC disconnect box. it's fully up to code, the disconnect box is five feet from the tub, and the guy they sent has done spas before, so he hardwired the line directly into the spa.

he did use my dryer breaker, so if i get an electric dryer i'll have to get my breaker box expanded.

it was a few hundred bucks, but i don't mind as the used spa was a great price and in great condition (seller getting a new one), and i feel safe and the electrical is secure and won't damage the spa or house wiring in the future

thanks for the above responses! it was heated up by Sunday, so made the miserable task of moving it well worth it.
 

SteveB

Usenet Archive
Joined
Oct 18, 2003
Messages
1,091
Reaction score
0
james said:
follow up - complete!

well we brought the enormous hot tub into my back patio, (through city fence which i repaired. was 7.5 x 7.5 by about 4' high - a nice size 5-7 person spa. also had to rotate it 90, not only that but raining steadily here in Denver all morning, but I didn't mind that, as the park my place backs up to was empty and no cars around - made backing in the trailer easier.

the electrical company, who i've used before, came saturday afternoon, same day - and rain a new four wire connect straight from my breaker box (see my above diagram), out to the patio. i have a disconnect box next to the AC disconnect box. it's fully up to code, the disconnect box is five feet from the tub, and the guy they sent has done spas before, so he hardwired the line directly into the spa.

he did use my dryer breaker, so if i get an electric dryer i'll have to get my breaker box expanded.

it was a few hundred bucks, but i don't mind as the used spa was a great price and in great condition (seller getting a new one), and i feel safe and the electrical is secure and won't damage the spa or house wiring in the future

thanks for the above responses! it was heated up by Sunday, so made the miserable task of moving it well worth it.
We love ours. You will love yours, too.

Steve
 

SQLit

Usenet Archive
Joined
Nov 4, 2003
Messages
2,237
Reaction score
0
james said:
follow up - complete!

well we brought the enormous hot tub into my back patio, (through city fence which i repaired. was 7.5 x 7.5 by about 4' high - a nice size 5-7 person spa. also had to rotate it 90, not only that but raining steadily here in Denver all morning, but I didn't mind that, as the park my place backs up to was empty and no cars around - made backing in the trailer easier.

the electrical company, who i've used before, came saturday afternoon, same day - and rain a new four wire connect straight from my breaker box (see my above diagram), out to the patio. i have a disconnect box next to the AC disconnect box. it's fully up to code, the disconnect box is five feet from the tub, and the guy they sent has done spas before, so he hardwired the line directly into the spa.

he did use my dryer breaker, so if i get an electric dryer i'll have to get my breaker box expanded.

it was a few hundred bucks, but i don't mind as the used spa was a great price and in great condition (seller getting a new one), and i feel safe and the electrical is secure and won't damage the spa or house wiring in the future

thanks for the above responses! it was heated up by Sunday, so made the miserable task of moving it well worth it.
dryer breaker?? Not a GFCI? or does the spa provide that protection?
 

Ask a Question

Want to reply to this thread or ask your own question?

You'll need to choose a username for the site, which only take a couple of moments. After that, you can post your question and our members will help you out.

Ask a Question

Members online

Forum statistics

Threads
144,907
Messages
1,592,101
Members
59,482
Latest member
lisac

Latest Threads

Top