Installing a small TT installation ... need to fit an earth rod … is
there any rule or decision factor that decides on the size to use …
standard 4’ rods come in 3/8” or 5/8”
Maximum current feed to installation is 32A
There is not "normally" a lot of difference in the thinner and thicker
rods performance but the thicker rods are physically more able to
drive straight if the ground contains stones etc. The ground
conditions do have a more considerable effect but your location is
critical to this, i.e. are you on dry well drained chalk or on
permanently damp clay.
You should ensure that the electrical characteristics meet the
requirements which will require at the very least an earth fault loop
impedance test carried out at the origin of your installation. Look
for less than 200 ohms to avoid instability due to drying/freezing. I
usually find the conditions in my location give between 20 and 40 0hms
(Loam over a bed of clay) but your situation may be completely
different.
It is also a good idea to use an earth rod chamber to make the final
connection to the rod as this will give protection and reduce the
surface voltage gradient in the event of a fault. It must provide
access to inspect the termination at intervals.
The conductor you use must be suitably selected/protected to avoid the
effects of corrosion and mechanical damage. Does your local library
have Regs Guidance notes in the reference section?