Wheelbarrowbob said:
It is a good idea to make your outbuildings a TT system which as you say
requires an earth electrode but use at least 16mm. As it is a TT system your
You probably won't need 16mm for the earth conductor (the earth loop
impedance of the spike is unlikely to be low enough to pass that much
current through it).
soket circuits need to be RCD protected to limit fault current although it is
not necsarry to rcd protect your lighting circuit. You need to test your spike
and it must be below 200 ohms, if not stick 2 in and retest. ( 200 ohms earth
fault loop impedence can result in high fault current before a mcb interupted
supply hence an RCD ) >Should I earth the consumer unit to an earth rod? If
so, what do I do
I think you have your "high fault current" and "high earth impedance
confused".
A high earth loop impedance (i.e. a "poor" earth) will result in LOW
fault currents - that is the problem. In a setup with a good earth
(typically one provided by the electricity supplier), should a fault
occur that allows the exposed metalwork of an appliance come into
contact with live, the current that flows to earth will be massive -
this is a "good thing" because it will cause the protective device
(fuse, MCB etc) to operate and cut off the current.
With a TT system that has a high earth loop impedance you can not rely
on this form of protection because the earth impedance may limit the
fault current to a level where it will not activate the protective device.
For example with a fault loop impedance of 100 ohms, your maximum fault
current on a live to earth short will be 2.3A - not even enough to trip
a typical lighting circuit breaker. This is why TT systems will need an
RCD in addition to fuses / breakers.
If you are using SWA just gland off the armour at each end and earth the cu to
the rod.
or use an insulated (i.e. plastic) consumer unit.