Does Federal Pacific stab and lock make tandem breakers?

Discussion in 'Home Repair' started by Aaron, Dec 18, 2004.

  1. Aaron

    Aaron Guest

    I have a Federal Noark panel. I would like to add 2 circuits, but only
    have one slot. I need to add a dedicated circuit for a dishwasher and
    would like to put in a GFI circuit breaker for the kitchen and
    bathroom.

    I have been unable to find a Federal Pacific stab and lock tandem
    breakers.

    I have also read Federal Pacific panels are a fire risk. Is this true
    and should I switch panels?
     
    Aaron, Dec 18, 2004
    #1
    hahasmart likes this.
    1. Advertisements

  2. Aaron

    SQLit Guest

    Federal lost its UL listing years ago. Yes it was for fires. I remember
    doing trouble calls in West Phoenix, when the full summer sun hit the
    panels, the breakers would trip.

    I can not tell you if you should change the service. That is going to cost
    some big bucks.

    This link will has 20-20 and 15-15 breakers listed.
    http://www.electricsupplyonline.com/prod/fpe-breakers.php
    Bring your banker for creative financing.

    Forget the GFCI breaker idea, MUCH more expensive. Go to your electric
    supply/box store and get GFCI outlets and install them. The kitchen and
    bathrooms should not be on the same circuit. Kitchens need 2 free circuits
    per code (at least) not counting installed equipment. Bathrooms as far as I
    am concerned should be on their own circuit. My SO has enough electrical
    stuff to make a small load bank. Thank god she can old plug in two items at
    a time. I did find a outlet expander in the bathroom once, after destroying
    it. I pleaded with her that I was not interested in dealing with a fire nor
    her death. I do not think that she really bought it but I have not found any
    more outlet expanders in the bathroom.
     
    SQLit, Dec 18, 2004
    #2
    1. Advertisements

  3. Aaron

    Speedy Jim Guest

    As SQLit said, put GFCI recepts in and forget about a GFCI breaker.

    Are FPE Panels risky? You betchum! And this story goes way back to
    the 60's.

    For a really detailed history:
    http://www.inspect-ny.com/fpe/fpepanel.htm

    Then you be the judge...

    Jim
     
    Speedy Jim, Dec 18, 2004
    #3
  4. Aaron

    RBM Guest

    You can get new circuit breakers made by the American Circuit Breaker Co.
    which fit the FPE panel and are U.L. approved. To my knowledge they don't
    make any half sized GFCI breakers, which like the others said, I wouldn't
    use anyway. You are better off with receptacles. Over all, if it were my
    house, I'd scrap the whole panel
     
    RBM, Dec 18, 2004
    #4
  5. Aaron

    Aaron Guest

    Thanks for the advice. I think I will look into switching out the
    panel. I worked as an electrical apprectice before graduating college.
    It has been about 10 years and I don't feel comfortable disconnecting
    a live panel. How do you get a panel turned off that does not have a
    main switch? Will the city kill your power for a day?

    Also when I was working I remember Square D panels being easier to work
    on then other brands, so I am thinking getting Square D. Any opinions?
     
    Aaron, Dec 18, 2004
    #5
  6. Aaron

    SQLit Guest

    When I was doing residential change outs that were fed from over head I
    would just cut the wires, hot, hot and then the messenger. I taped off the
    hots and made sure that they were different lengths. I would tie off the
    drop with an rope until I could get the new mast in place. Then using split
    bolts I would re connect the drop to the new riser. Not exactly for the fait
    of heart or to be done in a rain storm. Shingled roofs are not conductive.
    You need to get a permit from the local folks. I was doing so many that I
    was pulling 10 permits a week.

    Do not know about your neck of the woods. But here if you ask for the power
    to be shut off, there is no doubt that it will be off for at least 24 hours.
    The utility will not restore power until the AHJ has signed off. Some times
    48 hours for the clearance to get thought both parties. My customer were
    not interested in that kind of service.

    If your not comfortable with working live wires then get someone to do the
    job. Panel up grades can have lots of "gotcha's" if your not aware of the
    regs.
    Biggest one I see around here is the 2 ground rods that are needed, unless
    you have an ufer.

    Your home your choice of panels. I would look about and see what I could
    get the best deal on. Here in Phoenix the best place to buy residential
    change outs used to be Evergreen hardware. They actually had a kit all set
    up for a common installations.
     
    SQLit, Dec 18, 2004
    #6
  7. Aaron

    RBM Guest

    Killing power is different in all locations. Some places you can simply pull
    the meter, others you have to cut the overhead wires. Sounds like it might
    be a good idea to get some help. Square D is a nice choice for panels. They
    have QO type which is very good and homeline which is OK
     
    RBM, Dec 18, 2004
    #7
  8. Aaron

    Guest

    If you decide to get rid of that FP panel, send me an email. I'll
    give you a few bucks for the breakers, plus pay the shipping. I have
    a FP panel in my garage, and need to add a few circuits in the future.
    I have never had any problems with this panel, except the little tabs
    between the dual (220V) breakers tend to break, so they dont trip
    together. My main breaker just did that recently. I just drilled
    thru the lever and put in a cotter pin. Otherwise the panel works
    fine. I dont really see much difference in the panel itself, so
    apparently it must be the breakers themselves that cause problems.

    Email me here if you decide to do that. handyman AT centralpets DOT
    com.
     
    , Dec 19, 2004
    #8
  9. The problem appears to be that <some> original FP breakers fail to open
    when required on occasion, leading to fires. I also have FP in
    everything here on the place--who know from 20 to 40 years ago it was
    going to be an issue? So far every time they've tripped, but I continue
    to worry some...

    BTW, if you want used replacement FP breakers, they're "dime a dozen"
    item on eBay...
     
    Duane Bozarth, Dec 19, 2004
    #9
  10. Aaron

    Guest

    Thanks for the info. I looked at that web link in one of the replies
    on here. It appears I do not have the stab-lok type. I do recall
    seeing them though, with their orange painted handles. The ones I
    have in the garage are all the tan colored ones. That website did not
    seem to show the ones I have, so I am assuming I am safe, or hope so.

    I imagine ebay has them, but somehow I dont think I would get a
    bargain on there. New ones are only around $5 each. While I might
    find them on ebay for $2 each, I am sure the shipping would be $10 for
    each breaker. That just seems to be the way ebay is lately, so I dont
    even use it anymore unless I am looking for something that is obsolete
    or antique, and then i prepare to get robbed on the shipping and
    handling fees.

    I just thought I could get a bunch of them for cheap and give the OP a
    few bucks for what he would normally toss in the trash. I also like
    the idea of recycling. However, it looks like mine are a different
    type anyhow, and hopefully safer. I have seen plenty of these tan
    colored ones in use around this area.

    The Handyman
     
    , Dec 19, 2004
    #10

  11. Don't recall the specifics of the model names at present...eBay's like
    anywhere else, you simply have to be prudent. I bought a whole passel
    (something like 40 total mixed 110/220 for about $15 plus <$10 shipping
    that provided me enough spares for my lifetime...these happened to be
    mostly NOS from a retiring electrician with a few pulls. I did have to
    keep looking for a while, however. ymmv, obviously.
     
    Duane Bozarth, Dec 19, 2004
    #11
  12. Aaron

    Guest

    The only problem with Federal Pacific breakers is with the two ploe
    breakers. I have a FPE panel installed in 1962 and all the original
    single pole breakers work just fine (I load tested all of them). I
    bought a ground fault breaker off eBay that was fairly new and from
    Canada but I don't recommend them because they take up too much space
    in your breaker panel. I had no trouble buying used FPE breakers off
    eBay, but I got newer used ones with the white numbering, not the old
    ones with the red numbers on them).

    Now if your Federal Pacific panel has two pole breakers on it then loan
    test them by overloading one phase of it and see if it trips both legs
    properly. If it does than it's OK. The problem is that on a single
    phase overload on a 2 pole breaker it wasn't tripping the other pole.
     
    , Dec 20, 2004
    #12
  13. Aaron

    SQLit Guest

    I would be interested in how you really do load test your breakers. I have
    tested circuit breakers for a lot of years. We call it primary and secondary
    injection. Secondary injection is through the ct's. Your using the original
    breaker curve published by FPE?
    Our current supplies start out at about $15k for an MS-2 and crank well over
    $40k for a Doble unit.

    How do you test for LD and Instantous?

    snipped
     
    SQLit, Dec 20, 2004
    #13
  14. Aaron

    Speedy Jim Guest

    <SNIP>

    WRONG!
    Read all of the report:
    http://www.inspect-ny.com/fpe/fpepanel.htm

    One of the bigger problems with this design is the type of stab
    into the bus. It often results in high-resistance contact and
    resulting overheating.

    In minor cases, that can mean inconvenience when lights on one
    circuit flicker. In severe cases, it can end up with a melt-down
    of the panel.

    You have not truly lived until you've attempted to pry out an FPE
    breaker and had it crumble into dust in your hand....

    I used to think that testing of the breakers to ensure that they
    tripped was adequate assurance of an FPE panel suitability.
    No more.

    Jim
     
    Speedy Jim, Dec 20, 2004
    #14
  15. Aaron

    Tekkie Guest

    SQLit posted for all of us....
    We know he "load tests" them. Shorts hot to ground.

    Post info on the other stuff you posted, just curious...
     
    Tekkie, Dec 21, 2004
    #15
  16. Aaron

    Guest


    I still like having fuses for mains. I have them on my farm, and was
    going to eventually replace them until I ran into a burned up Square-D
    panel in a building I was demolishing. When I acquired that building,
    one of the first things I did was to get that panel before someone had
    a chance to steal it. I was a 100A panel, completely filled,
    including a few tandem breakers, and one 50A dual breaker to a sub
    feed, which was an old fuse box with at least a dozen fuses. I
    brought it home and what I found shocked me. The 100A main was siezed
    in the ON position, and I finally busted off the handle trying to
    force it to shut off. The 50A subfeed breaker worked, except it was
    welded to the bus bar and so badly charred where it connects to the
    bar that is fell apart. The two single breakers above and below that
    50A were charred from being in the same location. The other single
    breakers, and one 30A dual were all OK, That box was so overloaded, I
    am surprised there was not a fire. All I saved were those good
    singles and that one 30A dual. Everything else went in the trash.
    There was even charring around some of the neutral screws.

    I like single breakers, but for a main, I still think fuses are the
    safest.

    Mark
     
    , Dec 21, 2004
    #16

  17. ...all I know is that our FPE breaker panel is *expensive* to replace
    breakers and the lighting store strongly recommended that we replace
    the entire panel as soon as possible. It's the original panel that
    came with the house when it was built in the early 70's.

    We haven't experienced any problems with the panel but it's on our
    "to do" list for this spring.
     
    Capt Retardo and the Skidmarks, Dec 21, 2004
    #17
  18. Aaron

    Guest

    Uh oh....

    It's not a Federal Pacific box I have, its a Cutler Hammer. Guess my
    Alzheimers is starting........

    Never mind....

    At least I dont have to worry about a dangerous box.

    ------------------
     
    , Dec 22, 2004
    #18
  19. Aaron

    WyrTwister

    Joined:
    Apr 2, 2015
    Messages:
    65
    Likes Received:
    4
    I can not honestly say Sq D is the best brand of electrical equipment , but in my book , you can not find better .

    Wyr
    God bless
     
    WyrTwister, Jun 5, 2018
    #19