AWG needed for 68.5 amp 240 vac?

Bill C

Usenet Archive
Joined
May 16, 2000
Messages
6
Reaction score
0
Hello,

Can someone please tell me what AWG copper line is required to service a
68.5 amp 240vac tankless water heater? The manufacturer recommends an 80 amp breaker.

Thank you

Bill
 

TURTLE

Usenet Archive
Joined
Mar 3, 2000
Messages
12,351
Reaction score
0
Bill C said:
Hello,

Can someone please tell me what AWG copper line is required to service a 68.5 amp 240vac tankless water heater? The manufacturer recommends an 80 amp breaker.

Thank you

Bill
there is all kinds of type wire to choose from as distance of run and as in conduit or not and you can run it in # 6 to a # 2 by just what type wire it is and the metal the wire is made out of.

So if run in Copper wire run # 2 and you can't go wrong. the wire can be smaller if you tell the conditions like length of run , type of wire you have to use , and in conduit or out.

TURTLE
 

Doug Miller

Usenet Archive
Joined
Sep 11, 2002
Messages
4,265
Reaction score
0
Can someone please tell me what AWG copper line is required to service a
68.5 amp 240vac tankless water heater? The manufacturer recommends an 80 amp breaker.
Anywhere between #6 and #2. Depends on the temperature ratings of the conductors, and how they're installed (cable, conduit, etc).
 

RBM

Usenet Archive
Joined
Nov 22, 2004
Messages
5,194
Reaction score
0
There are variables but generally for what you're looking to do, number 4 THWN
 

Bill C

Usenet Archive
Joined
May 16, 2000
Messages
6
Reaction score
0
Thanks everyone. I don't like my subpanel setup. It's a big mess to upgrade and a long run in an old house to try to pull new wire. I'll just replace this failing tank water heater with another tank water heater.

Regards
Bill
 

Stormin Mormon

Usenet Archive
Joined
Aug 10, 2002
Messages
21,983
Reaction score
0
Also, copper versus aluminum makes a difference. I don't have a spec sheet, but alum takes a lower number. Which is a physically larger wire.

"Bill C" said:
Can someone please tell me what AWG copper line is required to service a
68.5 amp 240vac tankless water heater? The manufacturer recommends an 80 amp breaker.
Anywhere between #6 and #2. Depends on the temperature ratings of the conductors, and how they're installed (cable, conduit, etc).
 

zxcvbob

Usenet Archive
Joined
Jul 10, 2001
Messages
1,274
Reaction score
0
Stormin said:
Also, copper versus aluminum makes a difference. I don't have a spec sheet, but alum takes a lower number. Which is a physically larger wire.
He needs ampacity of 85A rather than 68.5 because it's a continuous resistive load. #3 Aluminum type SE cable will work if the breaker and terminals are rated for 90°C. Otherwise, he needs #4 copper rated for 75°C or better.

Best regards,
Bob
 

Ask a Question

Want to reply to this thread or ask your own question?

You'll need to choose a username for the site, which only take a couple of moments. After that, you can post your question and our members will help you out.

Ask a Question

Members online

No members online now.

Forum statistics

Threads
144,906
Messages
1,592,100
Members
59,482
Latest member
lisac

Latest Threads

Top