there is all kinds of type wire to choose from as distance of run and as in conduit or not and you can run it in # 6 to a # 2 by just what type wire it is and the metal the wire is made out of.Bill C said:Hello,
Can someone please tell me what AWG copper line is required to service a 68.5 amp 240vac tankless water heater? The manufacturer recommends an 80 amp breaker.
Thank you
Bill
Anywhere between #6 and #2. Depends on the temperature ratings of the conductors, and how they're installed (cable, conduit, etc).Can someone please tell me what AWG copper line is required to service a
68.5 amp 240vac tankless water heater? The manufacturer recommends an 80 amp breaker.
Anywhere between #6 and #2. Depends on the temperature ratings of the conductors, and how they're installed (cable, conduit, etc)."Bill C" said:Can someone please tell me what AWG copper line is required to service a
68.5 amp 240vac tankless water heater? The manufacturer recommends an 80 amp breaker.
He needs ampacity of 85A rather than 68.5 because it's a continuous resistive load. #3 Aluminum type SE cable will work if the breaker and terminals are rated for 90°C. Otherwise, he needs #4 copper rated for 75°C or better.Stormin said:Also, copper versus aluminum makes a difference. I don't have a spec sheet, but alum takes a lower number. Which is a physically larger wire.