Air Flow problem with 4 year old Gas furnance

Sean M

Usenet Archive
Joined
May 22, 2005
Messages
10
Reaction score
0
I have a four year old Bryant Plus 90i gas furnace (replacing the original gas furnace) and just recently had the same company add A/C. Part of the A/C install included a furnace tune up because there was some slight rattling and the thermostat would occasionally shut off completely. The installers tuned up the furnace but couldn’t diagnose the exact cause of the thermostat/furnace shut off problem. But during the troubleshooting we caught the error code that was briefly flashed on the thermostat (E2) and then determined the error code from the furnace’s LEDs (33). The E2 is a byproduct of the 33 code at the furnace as far as I can tell.

33 according to the manual is LIMIT OR FLAME ROOL-OUT SWITCH IS OPEN – Indicates the limit, rollout switch or auxiliary limit switch is open or the unit is operating in high heat only mode due to two successive low heat limit trips. Check for – Improper or misaligned limit and/or limit shield, Improper low heat gas input adjustment – Stuck high heat solenoid in gas valve.

They sent a service technician out to do further troubleshooting and he tried a new limit switch but it didn’t help. He was able to determine that the limit switch was tripping when the furnace cycled from High mode to low speed mode. His assessment was that there was inadequate air flow across the heat exchanger that is causing it to overheat.

Next week the original installer and the install manager are coming out to see what can be done to provide more air flow. My questions to any furnace installers out there are:

Should the installers have increased the size of the duct work in the garage that leads to the down stairs and upstairs registers and/or cold air return?

Is this something that is expected of reputable installers or do they just marry the new furnace to the existing duct work and assume all is well?

Is there are way to determine which part of the duct work is not providing enough CFM? My understanding is that it could be that the furnace is not getting enough cold air through the return or it cannot push out enough heat air to the registers. Can I determine which on is the problem?

What would you do to address this problem?

Thank you for any help you can provide.
 

Stormin Mormon

Usenet Archive
Joined
Aug 10, 2002
Messages
21,983
Reaction score
0
Get a different tech. Roll out doesn't have much to do with the fan blower or duct work that supplies heated air to the house.

Roll out is combustion air, and flue.

--

Christopher A. Young
Learn more about Jesus
www.lds.org
www.mormons.com

I have a four year old Bryant Plus 90i gas furnace (replacing the original gas furnace) and just recently had the same company add A/C. Part of the A/C install included a furnace tune up because there was some slight rattling and the thermostat would occasionally shut off completely. The installers tuned up the furnace but couldn't diagnose the exact cause of the thermostat/furnace shut off problem. But during the troubleshooting we caught the error code that was briefly flashed on the thermostat (E2) and then determined the error code from the furnace's LEDs (33). The E2 is a byproduct of the 33 code at the furnace as far as I can tell.

33 according to the manual is LIMIT OR FLAME ROOL-OUT SWITCH IS OPEN - Indicates the limit, rollout switch or auxiliary limit switch is open or the unit is operating in high heat only mode due to two successive low heat limit trips. Check for - Improper or misaligned limit and/or limit shield, Improper low heat gas input adjustment - Stuck high heat solenoid in gas valve.

They sent a service technician out to do further troubleshooting and he tried a new limit switch but it didn't help. He was able to determine that the limit switch was tripping when the furnace cycled from High mode to low speed mode. His assessment was that there was inadequate air flow across the heat exchanger that is causing it to overheat.

Next week the original installer and the install manager are coming out to see what can be done to provide more air flow. My questions to any furnace installers out there are:

Should the installers have increased the size of the duct work in the garage that leads to the down stairs and upstairs registers and/or cold air return?

Is this something that is expected of reputable installers or do they just marry the new furnace to the existing duct work and assume all is well?

Is there are way to determine which part of the duct work is not providing enough CFM? My understanding is that it could be that the furnace is not getting enough cold air through the return or it cannot push out enough heat air to the registers. Can I determine which on is the problem?

What would you do to address this problem?

Thank you for any help you can provide.
 

Ask a Question

Want to reply to this thread or ask your own question?

You'll need to choose a username for the site, which only take a couple of moments. After that, you can post your question and our members will help you out.

Ask a Question

Members online

No members online now.

Forum statistics

Threads
144,907
Messages
1,592,101
Members
59,482
Latest member
lisac

Latest Threads

Top