    Our two year old Trane XL1400 stopped working about a week ago. The
    hint was the aux heat was on nearly all the time - outside temp in the
    40's. I felt the "fat?" pipe coming out of the heat pump - it was
    cold. Measured the compressor motor current, it was about 7.7 Amps.
    Indicator LED was flashing once per second (normal).
    Called the service guy, when he opened the heat pump panel, the light
    was flashing 2 per second. First he thought it was the ambient temp
    sensor, went to his truck, came back saying he didn't have one with him
    but remembered the sensor was only used for cooling. He checked the
    fluid pressure, said it was OK. After a while he measured the motor
    coil resistance - it was open. Said it was a bad compressor and he'd
    have the guy in the office order a new one. I asked if it could be the
    motor internal protection being open. Maybe. Later, his boss calls,
    says leave the fuses disconnected so they can check in the morning
    after the motor has time to cool. It had been a few hours so I check
    the motor resistance and it looks OK so I start it up - no heat, motor
    current 7.7A, light still flashing 2X per second. Turn it off, decide
    to measure ambient temp sensor. In the process I disconnect and
    reconnect the main cable to the defrost control board - the light
    returns to one flash per second (normal), so I turn the whole thing
    back on and it works. Tech comes out next day and says everything
    looks OK, it must have been a clogged filter in indoor unit (I had just
    replaced it).
    Two days later, no heat. Tech comes out, intalls "fast start?" kit.
    No heat. Says compressor is bad.
    Finally, my question <g>: is it likely that the compressor is really
    bad? Given that it ran OK for a couple of days I'm a little confused.
    The motor current seems reasonable to me. Is it likely that the motor
    could be running OK but the compressor itself is bad? Also, although
    the tech is very pleasant, I'm somehow don't quite trust his diagnostic
    abilities yet. He seemed surprised when when turned the thermostat up
    4 degrees and the aux heat came on.
    They are to come out today and install a new compressor ($840 for
    labor).
    I'd appreciate any suggestions.
    gary64, Feb 1, 2006
  2. gary64
    Noon-Air Guest
    "gary64" <> wrote in message
    > replaced it).
    > labor).
    Before they touch the compressor, and bend you over for $840, tell them
    bring out a *REAL* tech and not just a compressor salesman, then call Trane
    and tell them everything you said here. You might also call another Trane
    dealer and get a second opinion... it might cost you $100 for the service
    call, but thats a lot better than $840.
    Noon-Air, Feb 1, 2006
  3. gary64
    Guest
    There are three types of "techs"...
    one is highly skilled , ethical....will take pride in diagnosing your
    problems and fixing the problem...he wont just bandaid it either...he
    will find the root cause of your trouble and make it right too.
    compressors just dont fail...there is a reason behind the failure....a
    good "technician" will find out why the compressor failed and will
    remedy the situation.
    Two..."tech" is more of a salesnician...he has minimal hvac
    troubleshooting training and is more familiar with selling you a new
    compressor or other part..... when he sticks his leak detector into the
    unit cabinet without removing doors and says it has a non repairable
    leak...its a salesnician... they can also be recognized by replacing
    multiple unrelated parts on a system with the excuse that ones failure
    caused the other....(" the compressor capacitor went bad and it fried
    your thermostat") Sometimes tech two is pushed into his situation by
    his employer...many employers pay on a scale based on what parts or
    equipment sales the tech generates...some provide bonus money on parts
    or equipment sold...this leads to greed on many a technicians part.....
    Third guy has a good heart but just lacks training...he wants to do a
    good job but he works for a hack outfit who provides no in house
    training and wont send the guys to school or even to the many supply
    house sponsered training sessions.
    He wants to find out the cause but just lacks the knowledge...a good
    kid...and would probably make a great tech one day if he gets some
    training.
    You have tech two or three....more than likely three...just an
    uneducated "technician"
    , Feb 1, 2006
  4. gary64
    gary64 Guest
    corny....
    I think you're right, he's a three. I just don't want to pay his
    tuition.
    > training.
    gary64, Feb 1, 2006
  5. gary64
    gary64 Guest
    I still have my basic question:
    "is it likely that the compressor is really
    could be running OK but the compressor itself is bad? "
    gary64, Feb 1, 2006
  6. gary64
    Noon-Air Guest
    Let me get this straight.... you do a hard reset on the defrost control
    board, then it starts working and you still want to replace the
    compressor??? Maybe if you called a *competent*, licensed, insured,
    professionally trained, HVAC technician to properly diagnose and repair the
    system, you will find that the problem has nothing to do with the compressor
    at all.
  7. gary64
    Bubba Guest
    Yes Gary. Your compressor is bad. Usually, a couple days before the
    compressor finally quits, it acts like yours has been doing.
    Sometimes, it does this several times before it quits all together.
    Do yourself a favor. Replace the whole system. Dont just replace the
    compressor or outdoor unit only. Get yourself a new 19 SEER heat pump
    with a variable speed air handler. Should only cost you around 10K
    which is a great deal because of the higher SEER ratings this year.
    You'll save tons of money and probably pay back your system in only 2
    years. It should save enough to take the family on a Hawaiian
    vacation.
    Bubba
    Bubba, Feb 2, 2006
  8. gary64
    Oscar_Lives Guest
    > replaced it).
    > labor).
    Your thermostat is shot. Replace it with a digital stat.
    Oscar_Lives, Feb 2, 2006
  9. gary64
    gary64 Guest
    Thanks for the responses:
    Bubba, this unit was installed in Aug 2002 - complete with variable
    speed air handler, etc etc. Its not 19 seer though. I'm not very
    knowledgeable about seer ratings but aren't they only about cooling?
    We use our air conditioning maybe 5 to 10 days a year. That's one of
    the reasons we live here (Pacific Northwest).
    I apolgize, I miss-stated the model number in my original post. Its a
    2.5 ton Trane XL14i. We also have a XL18. Both have digital
    thermostats. The smaller compressor failed in the XL18 after about 4
    years. I won't likely buy another Trane.
    My wife was in the process of composing a letter to the President of
    Trane when the local installation/service company called wanting to
    postpone the install of the new compressor - sick child at home. My
    wife let him know that she was writing to Trane and, in the process
    said she'd also send it to The Home Depot - the dealer works with Home
    Depot and has a space in the local store to sell Trane. That got his
    attention! He sent out his "senior" tech.
    This tech was obviously much more knowledgeable than the first. He
    went throught the entire system - starting with the indoor unit (in the
    attic, 60 ft of pipe from it to the outdoor unit). When he looked at
    the outdoor unit, he said it was 2.5 ton, the fan speed on the air
    handler was set for 2 ton. Next he hooked up his gauges, clipped on
    temperature sensors, and fired up the outdoor unit. Motor current was
    7.5 amps and it seemed to be working OK. After 15-20 minutes, he said
    the pressure was higher than he'd like (over 400 psi) so he shut it
    down, went upstairs and changed the dip switch settings on the air
    handler. Started the test again, pressure still rose to over 400 psi,
    then he bled some of the gas from the system. Finally, the pressure
    stayed under 400 (I don't recall reading). He said it really needs to
    be set under air conditioning conditions.
    Told me to watch it and call them if it failed again. There was really
    no need to tell me that <g>.
    So far, its still working (6 hours later).
    We'll see.
    gary64, Feb 2, 2006
  10. gary64
    Geoman^^ Guest
    I just popped in for a moment, I've been too busy to hang around here lately
    First, its not a Trane product. Did you know Trane has some of the LOWEST
    compressor failures in the HVAC industry?
    So, if you lost all these compressors it isn't Tranes fault, guess whos
    fault it is.
    1. Who ever hired the company who installed them, you or the general
    contractor who built the house is at fault for hiring hacks
    2. The installers either of the equipment or air supply is at fault, along
    with the designer of the system
    3. Probably brazed with no inert gas and caused all kinds of nasty things
    inside the copper refrigerant lines. This ruins compressors
    Thats your problem right there, HOME DEPOT!! Do you REALY think a dealer
    who knows his stuff will do work for them for half of what he makes with a
    regular install? Your going to see a lot of this in the future. NEVER buy
    technical stuff from a company who sells lumber!!!! You sound like you have
    a lot of money but no common sense! I'm not being insulting here, just
    honest! You go to a place where they pay thier people minimum wage, contract
    with dealers who have to give them a percentage of the sale and you expect
    quality?
    60 feet of pipe, I QUARANTEE that the pipe isn't sized correctly or has oil
    traps in it or kinks.
    When he looked at
    That means NOTHING! NOTHING NOTHING! Did he VERIFY the Cubic Feet per
    minute of air flow? I bet he doesn't even know how!
    How did he bleed the gas? What procedure did he use?
    YOU HAVE TO BE KIDDING ME!!!! This is the BEST TECH????
    THIS IS TERRIBLE, absolutly crimininal!!
    Paul, don't tell this guy to go away because this is really exciting to see
    how this 'best tech' is fixing this high COP heat pump!LOL
    So far the unit is STILL charged incorrectly, and soon enough due to it you
    WILL loose the compressor, and then you will blame Trane again.
    If you want to blame Trane, the only real thing you can do is tell them the
    truth, they make a great piece of equipemnt but they suck at selling
    equipment to those companies who should not even have a license.
    I make no false claim here, every experienced tech will tell you what I'm
    telling you is the truth, That company is a HACK and should be out of
    buisness!!! You ARE paying too much for energy, you ARE ruining your
    compressor, and if you continue to use this dealer your a fool, that is if
    what you say this guy did is true.
    Tell us where your at, there are good people on this group that CAN and will
    tune it correctly and tell you the truth about what needs to be done.
    > We'll see.
    Nothing to wait for, its a dead issue, litterally, the compressor is going
    to fail, period. I can't begin to number the offences that this jerk
    commited.
    Too tired to spell check, will stop back next week if possible.
    Geoman^^, Feb 2, 2006
  11. gary64
    Raines Guest
    <.p.jm@see_my_sig_for_address.com> wrote in message
    > Alt.home.repair, not here.
    He can post here if he likes...its an hvac forum brainiac
    > Click here every day to feed an animal that needs you today !!!
    > http://www.theanimalrescuesite.com/
    > Paul ( pjm @ pobox . com ) - remove spaces to email me
    > 'Some days, it's just not worth chewing through the restraints.'
    > 'With sufficient thrust, pigs fly just fine.'
    > HVAC/R program for Palm PDA's
    > Free demo now available online http://pmilligan.net/palm/
    Raines, Feb 2, 2006
    #11
  12. Damn right this is the proper place for the OP to ask quesions.
    Paul and his band of imbeciles should be ignored at all times and kill
    filed by everyone using this group.
    Imroves the signal to noise ratio remarkably well.
    And paul -- rant and rave in your pathetic existence -- you are killfiled
    in all your various combinations of addresses, so I'll never have to see
    your foolishness.
    How does it feel to know that you are a futile non entity?
    Jim McLaughlin
    Reply address is deliberately munged.
    If you really need to reply directly, try:
    jimdotmclaughlinatcomcastdotcom
    And you know it is a dotnet not a dotcom
    address.
    "Raines" <> wrote in message
    news:43e18b2e$0$25063$...
    > news:...
    Jim McLaughlin, Feb 2, 2006
    #12
  13. gary64
    Bob Guest
    OK, so you hired a hack like the asshole who told you not to post here.
    That's water under the bridge, where do you go from here?
    Unless I missed something, you have no obligation to this company. They
    tried to charge you $840 labor for a compressor you don't need. The "senior"
    tech may have actually removed refrigerant that first guy added. Did he let
    the refrigerant out into the atmosphere, or did he put it into a container
    when he "bled some of the gas from the system"?
    http://www.epa.gov/ozone/title6/608/subrecsm.html
    If you still have problems, ask friends and neighbors for recommendations
    and then call someone else. The new company should check to see if the
    system is installed to Trane specs, like properly sized refrigerant lines,
    proper duct work, proper refrigerant charge, etc.
    > We'll see.
    Bob, Feb 2, 2006
    #13
  14. gary64
    Geoman^^ Guest
    > You might want to follow through with the letter to Trane. This dealer
    > obviously doesn't deserve anything less than some personal attention
    > from them.
    Trane won't give a hoot about this, all they care about is keeping the
    plants open. Proof of this is the very real fact they started letting lumber
    yards sell their equipment! If this dealer sells equipment they wont do a
    thing about it.
    Also, remember in the late 80's, early 0's when GE was no more? In one city
    near Cleveland there were 3, yes THREE Trane dealers at one intersection,
    the other corner was vacant!!! This was near Marks old store that he use to
    work at~ So, Trane could care less about this dealer, they only want to
    keep their plants in operation and will do it no matter what.
    Its sad, but in my opinion they (the old GE) actually tuned the industry in
    for heat pumps back in the 70's and 80's. Then they didn't care any more.
    Lennox and others are training their dealers far superior than American
    Standard or Trane does. Its all about numbers.
    #14
  15. gary64
    gary64 Guest
    OK, you got my attention.
    We're near Hillsboro, OR 97123.
    Any recommendations?
    gary64, Feb 2, 2006
    #15
  16. gary64
    Guest
    >> from them.
    >thing about it.
    Rich, Its painfully obvious you know absolutely zilch about the Home
    Depot/Trane TCS program. Suggest first you learn the facts. Granted,
    certainly there are Trane Comfort Specialist Dealers who should not be
    in the program.
    Where were you when HD purchased Apex Supply in Atlanta? At the time,
    apex was one of the largest Trane distributors on the east coast.
    , Feb 2, 2006
    #16
  17. gary64
    RSESFSC Guest
    PLEASE FORWARD YOUR INFORMATION TO ME VIA E-MAIL AND I WILL HAVE THE
    APPROPRIATE FIELD SERVICE REPRESENTATIVE FROM YOUR AREA CONTACT YOU.
    THE 14 SEER UNIT THAT YOU ARE DISCUSSING IS A VERY RELIABLE UNIT AND
    UTILIZES A CLIMATUFF/DURATION SCROLL COMPRESSOR.
    OVER 50% OF COMPRESSORS RETURNED FOR AUTOPSY ARE MISDIAGNOSED.
    RSESFSC, Feb 2, 2006
    #17
  18. gary64
    Bubba Guest
    Yeah right. You are going to try and correct a problem when you cant
    even figure out how to turn your caps lock key OFF.
    Bubba
    Bubba, Feb 3, 2006
    #18
  19. "gary64" <> wrote in message
    I have one of those, and could fax you the charging charts if you've like
    lost yours...but pretty sure they're also pasted inside one a the panels.
    You can correctly charge it under either cooling or heat mode, either way no
    prob....
    IF the compressor will reliably start and pump up to 400 psi, then the
    compressor likely in perfectly good condition, FWIW.
    Sounds like maybe a stuck piston in the AHU to me...not enough info to tell
    for sure--nobody can see it from here...let alone even feel the pipes to
    tell where your heat is getting hung up at.
    Suggest get it running, and isolate the RV electrics.......then jumper so as
    to toggle from heat to cool mode several times with the compressor
    running--a good possibility that'll clear it up at least temporaily.
    All bets are off if the charge isnt currently reasonably correct though.
    SVL
    PrecisionMechanical, Feb 4, 2006
    #19
  20. gary64
    ~^Johnny^~ Guest
    On Thu, 2 Feb 2006 01:59:11 -0800, "Jim McLaughlin" <jim.mclaughlin>
    >your foolishness.
    Are you a newbie, or what?
    If you've filtered his posts, then why do you ask him a question?
    How are you going to read his reply?
    You might as well go ahead and filter me too, while you're at it,
    because I'm just as big of an asshoole as is Paul.
    Have a nice day.
    -john
    wide-open at throttle dot info
    ~^Johnny^~, Feb 7, 2006
    #20
  1. Susan
    Heat Pump vs. 2-Stage Heat Pump
    Susan, Dec 25, 2005, in forum: Home Repair
    572
    Susan
    Dec 25, 2005
  2. PrecisionMachinisT
    Free heat pump for parts, compressor is bad.
    PrecisionMachinisT, Apr 1, 2005, in forum: HVAC
    358
    Oscar_Lives
    Apr 2, 2005
  3. Susan
    880
    Bob Pietrangelo
    Dec 27, 2005
  4. Home Owner
    17
    453
    Raines
    Feb 16, 2006
  5. WVC17025
    2,002
    lp13-30
    Jun 1, 2006